1999It is mentioned in the 2002, I'm not sure if it is in an earlier version. 2002 is as far as I go back electronically.
The paragraph has a vertical line to its left.(2) Grounded Conductor. Where (1) an equipment
grounding conductor is not run with the supply to the build-
ing or structure, and (2) there are no continuous metallic
paths bonded to the grounding system in both buildings
or structures involved, and (3) ground-fault protection of
equipment has not been installed on the common ac service,
the grounded circuit conductor run with the supply to the
building or structure shall be connected to the building or
structure disconnecting means and to the grounding elec-
trode(s) and shall be used for grounding or bonding of equip-
ment, structures, or frames required to be grounded or bonded.
Changes in this 1999 edition of the National Electrical Code (as compared with the 1996 edition)
are indicated by vertical lines in the margin.