In a sticky situation and I greatly appreciate your advice regarding a recent inspection at our warehouse. We have 200amps, 3 wire (no neutral) feeding a Siemens P2 Panel, 480/277V, 3 phase, 4 wire. Engineer signed off on the 3 Phase, 3 Wire panel and stated no neutral is required, per the equipment coming off the panel. However, the inspector stated since the label from Siemens panel states 480/277V 3 Phase, 4W, the feeder cable must have a neutral. The Siemens panel does have a neutral bus/plate on it.
Inspector said we need to replace the panel, rather the inside part of the panel, so we can keep the breakers, etc. After spending half the day on the phone with suppliers, I came to the realization there are no 480/277, 3 phase, 3 wire panels on the market and it would take over a month to custom order. This is the last 'change' until our system goes live. Please note, the feeder bucket is nearly 200 ft away and rewiring with bigger conduit will be a big project.
The inspector cited NEC 110.3 both (A) and (B), comply with listing and labeling at panel 3 phase 4 wire requires a neutral to be installed.
What options do we have?
Is the inspector wrong? Is engineer wrong?
I did contact Siemens and we are trying to get a letter sent from them to inspector stating a neutral is not required and panel can function as wired.
I appreciate any input you may have about this situation. I will try to attach pictures.