Gentlemen,
This thread is very interesting, thanks for all the comments. I have, what I think is the same situation.
A "modern" house built around 1996? My friend is replacing the (E) Range with a brand new one. The cable feeding it(hardwired) is a 3 wire-2 hots and an Aluminum bare Neutral. I'm told it goes back to the subpanel which is on the outside of the house as a flush Meter Main with Distribution.
I'm assuming that the distribution/sub panel will have separate grounds and neutrals by code? The CB is 2p 50A, I will verify the
(E) wire size.
We will be adding an 50A 4 wire outlet and 40A? 4 wire Range cord("it fits"?). Waiting on verifying the Nameplate rating.
What I've gathered from your comments is:
1. Phase bare neutral white.
2. Connect bare neutral, in distribution panel, to the neutral buss.
3. Run a "#10 ECG to any accessible point on the grounding electrode and convert it to a 4 wire. "
The house has a concrete slab?, cabinetry, an abandoned PVC conduit in the slab- going somewhere? etc.
What are some options for finding that grounding point? Can I take it to a nearby receptacle/switch box and attach it to the ground wires in that box?
Any other suggestions?
Thanks! Tom