Senior Member
If a sub-panel is for 240 volt loads only, is it a violation to feed it with only 3 wires? (No Nuetral)
No problem if it is past the service equipment. This is a design issue but I would take a neutral "just in case".davedottcom said:If a sub-panel is for 240 volt loads only, is it a violation to feed it with only 3 wires? (No Neutral)
charlie said:No problem if it is past the service equipment. This is a design issue but I would take a neutral "just in case".![]()
C3PO said:I agree. If you don't run the neutral than someone will just use the EGC for the neutal later.
davedottcom said:They would be guilty of a violation, but is the 3-wire sub panel a violation if clearly marked "240 Loads Only - No Neutral Available"?
The marking is not a violation of the Code. ;-pdavedottcom said:is the 3-wire sub panel a violation if clearly marked "240 Loads Only - No Neutral Available"?
davedottcom said:They would be guilty of a violation, but is the 3-wire sub panel a violation if clearly marked "240 Loads Only - No Neutral Available"?
al hildenbrand said:Consider a service supplying 208/120 3? to a building where the tennant brings in a bunch of single phase 240 volt loads (imagine woodworking shop).
When I set a boost autotransformer, I can supply 240 Volt to a sub panel but I can't get a neutral.
If the design doesn't require a neutral, why penalize the customer with a higher bill?
al hildenbrand said:The marking is not a violation of the Code. ;-p
Nope, but nice to have (sorta like the neutral if it is needed at some time in the future). Really now, a neutral takes some material and a touch more labor but marking a panelboard with a permanent marker inside the cover is free. :smile:davedottcom said:Do you mean the marking is not required?
I apologize if my twist of the phrase missed my intended mark. As you wrote your question, I read that the label "240 V only - no neutral", itself, would be against Code.davedottcom said:Do you mean the marking is not required?
al hildenbrand said:I apologize if my twist of the phrase missed my intended mark. As you wrote your question, I read that the label "240 V only - no neutral", itself, would be against Code.
Used to be, awhile back, we had a smilie choice of a "Razz", a little face sticking its tongue out. ;-p
That one's OK, but I liked the one that an earlier version of the UBB code supported. As I recall, the tongue went in and out, and included a sense of "wryness".480sparky said:Ya mean a?![]()
al hildenbrand said:That one's OK, but I liked the one that an earlier version of the UBB code supported. As I recall, the tongue went in and out, and included a sense of "wryness".
Yup. This smilie has the gist of my recollection.480sparky said:So one more like?![]()