3-wire subpanel question

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Old sub panels in detached buildings had a 3 wire cable feeding them with a ground rod. I run into these all the time. I have to relocate a sub panel and have no choice but to continue using their same method. It bothers me that it does not meet modern code, having four wires. But I don’t know what else to do.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
As long as there is no parallel neutral path back to the main building there is not a problem. The reason for the new requirement is basically the potential for human error like adding a phone line or coax but since both of those are pretty much obsolete there is less of a chance now for parallel paths although not unheard of.
 
Old sub panels in detached buildings had a 3 wire cable feeding them with a ground rod. I run into these all the time. I have to relocate a sub panel and have no choice but to continue using their same method. It bothers me that it does not meet modern code, having four wires. But I don’t know what else to do.
IMO the old way is better, typically there is a larger fault path conductor with the 3 wire where it's a combo neutral and fault path conductor.
 

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
As long as there is no parallel neutral path back to the main building there is not a problem. The reason for the new requirement is basically the potential for human error like adding a phone line or coax but since both of those are pretty much obsolete there is less of a chance now for parallel paths although not unheard of.
Thank you
 