I'm helping a builder buddy of mine build a house for a couple and there is a meter/main on the exterior wall. It has a 200 amp breaker and has knockouts available for more breakers. Inside there is a 200 amp Eaton panel. The meter and interior panel are back to back and connected with pvc conduit.
When it was determined that the meter would have a main breaker I told my friend that the interior panel would now be a sub panel and need neutrals and equipment grounds separate, float the neutrals, bond the EGCs to the enclosure, run 4 wires between meter and interior panel.
Long story short, he ran his usual set-up. Service Entrance conductors between the two. No EGC. As he is making up the panel he asks me if he needs to connect the bonding strap. I told him that technically this is now a sub panel, needs 4 wires, etc....gave the whole spill again.
He's not running a 4th wire. Period.
So I told him under the circumstances, YES, connect the bonding strap because if you don't and someone adds a ground bar, those EGCs won't the bonded to the neutral and there will not be a path to trip the breaker, and if the panel enclosure became energized the strap will provide a path to trip the breaker.
Do you agree with my assessment?
When it was determined that the meter would have a main breaker I told my friend that the interior panel would now be a sub panel and need neutrals and equipment grounds separate, float the neutrals, bond the EGCs to the enclosure, run 4 wires between meter and interior panel.
Long story short, he ran his usual set-up. Service Entrance conductors between the two. No EGC. As he is making up the panel he asks me if he needs to connect the bonding strap. I told him that technically this is now a sub panel, needs 4 wires, etc....gave the whole spill again.
He's not running a 4th wire. Period.
So I told him under the circumstances, YES, connect the bonding strap because if you don't and someone adds a ground bar, those EGCs won't the bonded to the neutral and there will not be a path to trip the breaker, and if the panel enclosure became energized the strap will provide a path to trip the breaker.
Do you agree with my assessment?