Well, Ive seen it again. Where someone had done a remodle and they rerouted some circuits and they had put some #12 on a 30 amp breaker!! there were some outlets out of power and I traced it back to a panel, (that was mislabled) and the 30 amp had tripped!! thank goodness that the #12 never over heated. How often do you run into this??
 

Jim W in Tampa

Senior Member
Location
Tampa Florida
Well, Ive seen it again. Where someone had done a remodle and they rerouted some circuits and they had put some #12 on a 30 amp breaker!! there were some outlets out of power and I traced it back to a panel, (that was mislabled) and the 30 amp had tripped!! thank goodness that the #12 never over heated. How often do you run into this??
usually after the fire.
 

Mule

Senior Member
Location
Oklahoma
We just did a service and panel upgrade on a older home and found the same thing going to a package HVAC unit. So we put a 20 brk on it and told the owner we could not re-install a 30 on it. Told him to call us if it trips and we'll replace it with #10.....Bet it trips !!

BTW...isnt #12 actually good for 25amps without the astrics????
 
Last edited:

Rewire

Senior Member
We just did a service and panel upgrade on a older home and found the same thing going to a package HVAC unit. So we put a 20 brk on it and told the owner we could not re-install a 30 on it. Told him to call us if it trips and we'll replace it with #10.....Bet it trips !!

BTW...isnt #12 actually good for 25amps without the astrics????

Are you an electrician?
 

stickboy1375

Senior Member
Location
Litchfield, CT
We just did a service and panel upgrade on a older home and found the same thing going to a package HVAC unit. So we put a 20 brk on it and told the owner we could not re-install a 30 on it. Told him to call us if it trips and we'll replace it with #10.....Bet it trips !!

BTW...isnt #12 actually good for 25amps without the astrics????

Your situation was probably legal....
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
We just did a service and panel upgrade on a older home and found the same thing going to a package HVAC unit. So we put a 20 brk on it and told the owner we could not re-install a 30 on it. Told him to call us if it trips and we'll replace it with #10.....Bet it trips !!

BTW...isnt #12 actually good for 25amps without the astrics????
It's possible that it was a code compliant installation. Depending on the nameplate data, No. 12 conductors with a 30A OCPD may have been fine.
 

Mule

Senior Member
Location
Oklahoma
It's possible that it was a code compliant installation. Depending on the nameplate data, No. 12 conductors with a 30A OCPD may have been fine.


Didnt read the nameplate on the unit.....We installed a rain tight HOM panel nex to the meter base that was around 20ft from the HVAC unit....No service disconect or other protection on the unit itself..
 

Mule

Senior Member
Location
Oklahoma
Yep... I think its funny when people size the wire to the MAX. OCP... WHY do people do this?

Guilty......OK...Im stubborn, as you all know..but humble...:smile:v.I've never dug into this in the code book. But on the surface, I dont see how you could install a larger breaker on a branch circuit than normally allowed, reguardles of the HVAC units contribution to the situation.....????
 

stickboy1375

Senior Member
Location
Litchfield, CT
Guilty......OK...Im stubborn, as you all know..but humble...:smile:v.I've never dug into this in the code book. But on the surface, I dont see how you could install a larger breaker on a branch circuit than normally allowed, reguardles of the HVAC units contribution to the situation.....????

Because the breaker is not providing the OCP, only ground-fault and short circuit protection.
 

peter d

Senior Member
Location
New England
Guilty......OK...Im stubborn, as you all know..but humble...:smile:v.I've never dug into this in the code book. But on the surface, I dont see how you could install a larger breaker on a branch circuit than normally allowed, reguardles of the HVAC units contribution to the situation.....????

Because the breaker only protects the wire from short circuits and ground faults. A SC or GF will be in the range of 1000's of amps and will trip any breaker assuming correct settings and coordination (not an issue for residential.)

The unit itself is protected by thermal overloads in the motors.
 

Mule

Senior Member
Location
Oklahoma
Duh, I was always taught that the branch circuit protective device protects branch circuit conductors only....
 

stickboy1375

Senior Member
Location
Litchfield, CT
if you look close at the MCA and max CB you will find the MCA will be 80% of the max breaker size.



Here is an easy picture to follow...

ACRefrigerationEquipementNameplateR.jpg


AC & Refrigeration Equipement Nameplate Rating.jpg
 
Last edited:

Jim W in Tampa

Senior Member
Location
Tampa Florida
Guilty......OK...Im stubborn, as you all know..but humble...:smile:v.I've never dug into this in the code book. But on the surface, I dont see how you could install a larger breaker on a branch circuit than normally allowed, reguardles of the HVAC units contribution to the situation.....????

and when or if they call you back will you charge them to put back what was legal ?
 