I know you are allowed 175% of the circuit amps I was just saying what I see in the field alot
 
I alway had it in my thick skull that a hacr rated breaker allowed for start up current, and then everything was normal #10/30amps etc......or whatever the unit called for....
 
I alway had it in my thick skull that a hacr rated breaker allowed for start up current, and then everything was normal #10/30amps etc......or whatever the unit called for....


I generally use this rule of thumb. Wire size to minimum circuit ampacity, OCPD size to maximum size listed.
 
I alway had it in my thick skull that a hacr rated breaker allowed for start up current, and then everything was normal #10/30amps etc......or whatever the unit called for....

Never wondered why AC units had Minimum Circuit Ampacity AND Maximum Breaker Size?



Let me ask you this, how would you size a 1HP motor for a well pump?
 
I generally use this rule of thumb. Wire size to minimum circuit ampacity, OCPD size to maximum size listed.

I've always sized both the wire and the branch circuit device to the min circuit ampacity on the nameplate, and never had a issue.:-?
 
Well, Ive seen it again. Where someone had done a remodle and they rerouted some circuits and they had put some #12 on a 30 amp breaker!! there were some outlets out of power and I traced it back to a panel, (that was mislabled) and the 30 amp had tripped!! thank goodness that the #12 never over heated. How often do you run into this??

Did a service upgrade from an old fused service (after one of the fuse holders caught fire).

EVERY circuit had a 30 amp fuse. All were #14, except 1 #12.

After the tenants then complained about the kitchen circuit tripping, we gave the landlord a price to add some circuits. The (1) #14 circuit had: kitchen and dining room lights, dishwasher, disposeall, all kitchen receptacles, including fridge and microwave, and the detached garage.

Still haven't heard back on that one. :roll:
 
Never wondered why AC units had Minimum Circuit Ampacity AND Maximum Breaker Size?
That's where I went wrong as I thought the hacr rated breaker allowed for the additional current...

thanks guys...see there you can "teach a ole Mule new tricks"......:D
 
You wont when they are brand new units, but over time there could be.

I think he meant minimum OCPD size, not MCA. In other words, if the min. OCPD is 40, #8 wire. Is this correct Mule?

In any event you haven't done any harm - you just have an oversized wire which is good for voltage drop, but not necessary.
 