That's true for a single phase secondary, but with a center-tapped delta secondary, imbalance can lead to transformer overload even when all the load currents are less than the transformer rated current, due to additional circulating current. See https://forums.mikeholt.com/threads...-of-3-phase-transformer.2582774/#post-2941681 for the details.Why would a transformer care if only one side of a center tap was fully loaded?
"That's true for a single phase secondary,"
which is where this discussion started.......no doubt there are 'concerns' that "with a center-tapped delta secondary, imbalance can lead to transformer overload " but we have strayed from the original question of whether or not 30 amps of neutral current is necessarily a Bad Thing