Frank DuVal
Senior Member
- Occupation
- Electrical Contractor, Electrical Engineer
That's true for a single phase secondary, but with a center-tapped delta secondary, imbalance can lead to transformer overload even when all the load currents are less than the transformer rated current, due to additional circulating current. See https://forums.mikeholt.com/threads...-of-3-phase-transformer.2582774/#post-2941681 for the details.Why would a transformer care if only one side of a center tap was fully loaded?
"That's true for a single phase secondary,"
which is where this discussion started.......no doubt there are 'concerns' that "with a center-tapped delta secondary, imbalance can lead to transformer overload " but we have strayed from the original question of whether or not 30 amps of neutral current is necessarily a Bad Thing
Based on what? Poor circuit placement in the panel? Who's to say later the homeowner or for whatever reason someone needs to juggle a repair, moves them and some how all 3 kitchen 20s, 20amp the outlets in the basement and the 20amp feeding the garage are all riding the same phase? And its January, running an electric heater in each, the toaster, and the microwave?IMO you would need to work at getting a sustained imbalance of 30 amps.
If its not a big deal to be out of balance and dumping amperage down the neutral, then why the efforts to stay as close to balance?
Actually, 70 AMPS!
QO170
Editing to try and remove need to download page to read..... hold on....
Ok.Wow. Name one practical real world application that's hungry for a single leg of 70 amps @ 120v? I cannot think of one.
Actually let's call it 56amps with the 80% rule. Still, even with inrush, its still alot.
In the off grid world, we used to have a lot of 120 volt only inverter systems, that had several inverters in parallel. Sometimes if you needed a larger breaker, you would use one side of a double pole of some kind, or something like this QO170.Wow. Name one practical real world application that's hungry for a single leg of 70 amps @ 120v? I cannot think of one.
Actually let's call it 56amps with the 80% rule. Still, even with inrush, its still alot.
That's how I would do it.Ok.
You only have one space left in your SE panel. You need 50 amps of 120 volt lighting for your Holiday display. Five 15 amp circuit breakers arranged in a newly installed six circuit MLO panel.
120 volt branch circuit may not be so likely, feeder more of a possibility, particularly if only 120 volts is available for whatever reason.Wow. Name one practical real world application that's hungry for a single leg of 70 amps @ 120v? I cannot think of one.
Actually let's call it 56amps with the 80% rule. Still, even with inrush, its still alot.
With a random 50/50 coin flip for each circuit, the chances that five circuits end up on the same leg are 1/32 to begin with. Then multiply that by the likelihood someone loads them all up at the same time as you describe, with no load on the other leg, and the chances of this happening by random luck are a small fraction of 1%. Most houses would never use 3.6kW in 120V loads at all at once anyway.Based on what? Poor circuit placement in the panel? Who's to say later the homeowner or for whatever reason someone needs to juggle a repair, moves them and some how all 3 kitchen 20s, 20amp the outlets in the basement and the 20amp feeding the garage are all riding the same phase? And its January, running an electric heater in each, the toaster, and the microwave?
What effort? The vast majority of residential electricians make no such effort whatsoever.If its not a big deal to be out of balance and dumping amperage down the neutral, then why the efforts to stay as close to balance?
Is it a big concern or not?
Yes, why not?Can one per code install a subpanel with 1x50 amp single pole 120v conductor? I thought 2 open spaces were required for future install?