Typically, if it's easily removable then it's a cover not a door. You measure the working space of a covered enclosure after removing the cover completely. You measure the working space of a door enclosure with the door fully open.
I don't believe the 90 applies to operating that sort of door. It applies when you remove the whole cover for service.
If you remove the cover there is no need for a 90 degree opening requirement, cover should be laying wherever you set it.
Is there a minimum depth requirement for a door that does not expose you to live parts when opened?
Good design practice may consider this, but I don't believe it is a code problem.