But cables are supporting cablesI would allow it. Cable ties are permitted to secure NM cable.
Yup and it's a judgement call as to whether or not that cable tie will hold the cable better than a Stacker. A Stacker on a flat cable like 12/2 or 14/2 NM cable is useless, you can pull the cable right out.But cables are supporting cables
OK........So tell me, what's the difference between using stackers and the wire tie method? I don't believe there are any grave, negative effects from either method.Why, yes. Yes, it is. They work well for LV, too.
View attachment 2553715 View attachment 2553716 View attachment 2553717
I agree with you. But common sense tells me that in a 23 cubic inch box, 4, 12-2 NM B cables and a duplex receptacle easily fit with room to spare. Perhaps the NEC Gods should ease up the gospel a bit and let common sense factor in.If you have a device in that box then you have a fill violation with 4- 12/2 cables
Nope, other than what's stated in post #9.OK........So tell me, what's the difference between using stackers and the wire tie method? I don't believe there are any grave, negative effects from either method.
I agree also, but allow me a moment please...I agree with you. But common sense tells me that in a 23 cubic inch box, 4, 12-2 NM B cables and a duplex receptacle easily fit with room to spare. Perhaps the NEC Gods should ease up the gospel a bit and let common sense factor in.
The difference is one cable is not dependant on another cable in the stacker but in the OP picture the ty-wrap'd cable is dependant on the cable it's being tied to. I'm not saying there is anything unsafe with the ty-wrap, it's just a code violation as the code is written, but I would not have a problem with it.OK........So tell me, what's the difference between using stackers and the wire tie method? I don't believe there are any grave, negative effects from either method.