300.13 b
Smart $
Esteemed Member
Ohio
monkey_man_100 said:
I guess it didn't work
Your image source URL is "http://http://groups.msn.com/supercalafrajalistickespyaladosioius"
That is neither a valid URL (one too many "http://") nor a valid image.
Also noticed there is no longer an attachment feature in my Advanced Post interface. Is this the case for everyone?
stickboy1375 said:
Your talking about two seperate wires entering a box and using all the screws on the device correct? Without using pigtails...
yes. I have a book by Ray C. Mullin and it has a diagram with two pictures. One outlet with pigtails and one without. He then sites 300-13 (b)
Sorry I am having trouble showing what I mean. And I don't know how to use that Msn group thing.
stickboy1375
Litchfield, CT
Well if the picture with pigtails is a MWBC then the book is correct.. :)
Ok I think I am starting to understand. I was confused cause I thought that you had to use a pigtail in every box that had more than one wire, for instance two 14-2 romex conductors in a single gang box. SO you could just back stab all 4 wires and put the grounding wire where it goes. I hope I am not too confusing. It is a lot easier to show what I mean in person.
George Stolz
Windsor, CO NEC: 2017
Service Manager
You've got it. :)
The term "multiwire branch circuit" is an NEC-defined term, so whenever they use it, they are using the term as an abbreviation for the long definition of that term, every time they use it.
That term, taken literally in english would mean "a circuit with many wires."
When the NEC uses the term, it means "two or more hots on different phases that are sharing a neutral back to the panel."
George Stolz
Service Manager
every receptacle I have seen have 4 screws.Still ok? I hate to beat this subject down but I like to be sure.
As long as you only install one wire per screw (as the receptacle is listed) and none of the wires are bigger than #10 (110.14(A)) then you are fine.
Bear in mind, there is more peace of mind in using a wirenut instead of the receptacle for this purpose, and it is generally considered a superior practice. But IMO, the screws are just fine, and they're what I use.
drg
"Good "now that the soild wire thing is over what do you guys do different when using stranded wire ???
don_resqcapt19
Illinois
retired electrician
drg,
From the UL Guide for recptacles (RTRT).
Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.
Don