300.14

gcushman

New User
Location
04071
Occupation
electrician/instructor
In NEC 300.14, what is the meaning or definition of "free conductor"? Does this mean no terminations before the 6" length? If so, does mean that the EGC can not wrap around a ground screw before the 6" length?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In NEC 300.14, what is the meaning or definition of "free conductor"? Does this mean no terminations before the 6" length? If so, does mean that the EGC can not wrap around a ground screw before the 6" length?
This has been argued but IMO as long as you have the appropriate length of wire after any connection then you would be compliant
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This has been argued but IMO as long as you have the appropriate length of wire after any connection then you would be compliant
I agree and unless he's changed his mind apparently so does Mike Holt.
ecmweb_3074_250_s148c_01_un250_s196web2.png
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In my opinion, the required length only applies before you make the splice or termination, and it can be any length after you do that.

It doesn't really make any difference any more since the 2023 code added the following:
The 150 mm (6 in.) free conductor shall be permitted to be spliced or unspliced.
 