dan 456
Member
- Location
- nyc,ny,usa
Been reading posts on here for quite awhile, first new thread I am starting. Service 3 phase 4 parallel 500 kcmil. conductors entering the end line box phase isolated. The conduit is fre with a change to gal for 3 feet entering the end line box. ( a pre fab 90 and short nipple) the conduits enter the end line box with lock nuts and migbs. power company said this is no good with isolated phase entry because conduits must be non ferrous for the entire length. my question. are there other ways to do this with either cutting slots in the conduit or cabinet, an isolation plate installed between the conduits and box or an open bottom box where the conduits are less than 3" into the box? last, I understand the heating issue, hysteresis and the need for the non ferrous conduit, but what is the heating concern? is it because of the short distance of gal pipe or is it that this gal is grounded and bonded to the box? another words would this install be ok if the pipe was isolated from end line box or they want no metal pipe what so ever? any advice much appreciated