sparkyrick
- Appleton, Wi
Kinda funny that the AHJ nitpicks about a receptacle that isn't required at the landing, but will allow foreign wiring in the elevator shaft to rectify his nitpick.
:thumbsup: I'll stand next to you.
I had a guy add receptacles to a full granite back splash in a kitchen and two in a bedroom, where he made the closet wall space instead of a closet. This was at final and when he started screaming and hollering that it had been approved at rough, I said were you cabinets in at rough, if not how was the inspector supposed to know where you exactly needed receptacles and don't your plans call for a closet in the other room? No and yes were his answers. Do you know where receptacles are required? Yes. Well then, they were approved at rough, yes, by another inspector, don't have the electrical inspector come out at final and think that I'm going to sign it.
First off....the GC communicated with the AHJ as to how to resolve the problem of no receptacle on the landings. The AHJ told the GC that the elevator shaft could be utilized for the installation of the outlets provided they were in conduit. I have complied with the AHJ on all occasions and don't see how I am at fault with what should have been a non issue to begin with.
I will give you the the situation with the cabinets, but not a hallway (if that is what the OP's space is deemed to be), that should have been caught at rough in. How to handle it, I don't know, I understand the inspector is human and can make mistakes, but why is someone else's mistake supposed to be my fault? This is a situation where if I were the OP, I would have figured it passed rough in because it was determined not to be a hallway therefore no receptacle required. There is no cabinets added later to make it look different at rough then it looks at finish time, this should have been addressed at rough in time, or even plans review time if in an area where they do that.
I think OP did know a hallway needs a receptacle, but did not see this as a hallway and inspector said nothing at rough in. Now inspector is insisting this is a hallway, and is throwing his authority around on this one. What will this guy say when someone points out his solution creates other code violations??
Well it's very likely that the inspector didn't say anything at rough, but then it's just as likely (since it happens here) that his boss or superior followed behind him to make sure that he was doing his job and told him to have a receptacle installed.
Luckly, I'm the superior for electrical and my bosses don't know much about it, but they still go out from time to time, just to check on things. I missed the ADA height requirement on all of the exterior fixtures on a resturant one time and my boss had me move them up at final.
What ADA fixture requirement is there about height of a fixture? are you referring to receptacles?
In a path of travel the lowest point of the fixture has to be a least 80" above the ground unless the fixture does not extend more then 4" into the path.
I would think the foot candles at the walk area would be the most important thing to consider with ADA regardless of what or where the light source is.
(I can see a little) what they may be getting at with height, but that can be offset by additional illumination from different angles.
Compensating light levels will not affect anything. The are talking a bought walking with the sweep of a Cain to guide you. Objects 27 in or lower in height will be detectable with the Cain sweep. If your over 80 in you wont bumb your head. So anything between 27 in to 80 cannot obstruct more than 4 in off the wall
funny I have never seen a person using a cane poke around that high.
I do not see any exception for residential.
620.37 Wiring in Hoistways, Machine Rooms, Control
Rooms, Machinery Spaces, and Control Spaces.
(A) Uses Permitted. Only such electrical wiring, raceways,
and cables used directly in connection with the elevator or
dumbwaiter, including wiring for signals, for communication
with the car, for lighting, heating, air conditioning, and ventilating
the elevator car, for fire detecting systems, for pit sump
pumps, and for heating, lighting, and ventilating the hoistway,
shall be permitted inside the hoistway, machine rooms, control
rooms, machinery spaces, and control spaces.
Go figure, AHJ wants a receptacle on a stairway landing which by his interpretation is a hallway and doesn't care if an actual cited code is violated to achieve the end. (headslap)
The point to that post was that wiring feeding something outside and non-associated with the elevator or the hoistway was routed inside the hoistway. This would be prohibited by the section mentioned.I don't think the landing or the stairs are in the hoistway. Can you see and touch the elevator car from the stairs as it moves up and down?! I suspect the elevator hoistway is enclosed within walls that are then surrounded by the stiarway.