I have an existing MTS that I believe is in violation of 300.3. Normal power comes in with just 2 4/0's. I believe there is an exception for switches that allows this install without the grounded conductor run with them. I cant find this exception in 300 or 400. Where is it???
The load leaves in the same nipple but with the 4/0's and the #3 grounded conductor from the generator inlet device goes to the MDP. This I believe is in violation.
Also, I need to submit a riser diagram to the building dept on Monday. How would you list the conductors in that conduit??? 4-4/0's, 1-#3, and 1-#4EGC in 2" conduit???
Thanks
The load leaves in the same nipple but with the 4/0's and the #3 grounded conductor from the generator inlet device goes to the MDP. This I believe is in violation.
Also, I need to submit a riser diagram to the building dept on Monday. How would you list the conductors in that conduit??? 4-4/0's, 1-#3, and 1-#4EGC in 2" conduit???