300.4 d

Status
Not open for further replies.

garrisonm1

Member
Location
Maryland
I have a 4 gang nail in carlon box, I had one 14/3 and 2------- 14/2 wires running down the stud to this box, the 2---- 14/2 cables were under one staple. Inspector made me change this because the wires weren't in the center of the stud. I did it with no objections, but i didn't think the 1 1/4 rule applied to this.
 
but i didn't think the 1 1/4 rule applied to this.

IMO it does. Here is exhibit 300.3 from the 08 NECHB. Note the top center example.

3004D.jpg
 
I have a 4 gang nail in carlon box, I had one 14/3 and 2------- 14/2 wires running down the stud to this box, the 2---- 14/2 cables were under one staple. Inspector made me change this because the wires weren't in the center of the stud. I did it with no objections, but i didn't think the 1 1/4 rule applied to this.

The 1 1/4 rule applies to any cable that encroaches into this restricted space. If the space was free, then 2 flat cables can be stapled one over the other but not on edge.
 
I have a 4 gang nail in carlon box, I had one 14/3 and 2------- 14/2 wires running down the stud to this box, the 2---- 14/2 cables were under one staple. Inspector made me change this because the wires weren't in the center of the stud. I did it with no objections, but i didn't think the 1 1/4 rule applied to this.

Sure it does that's why they make these
4015948.jpg
 
Im more of a commercial electrician and we use cj6, for mc cable, thats fine and dandy but what doesn't make too much sense is when you use a deep plastic carlon box thats 3 1/4 inches deep , the back of the box is only a 1/4 inch away from the other side of the wall and the cables have to enter there regardless.
 
Im more of a commercial electrician and we use cj6, for mc cable, thats fine and dandy but what doesn't make too much sense is when you use a deep plastic carlon box thats 3 1/4 inches deep , the back of the box is only a 1/4 inch away from the other side of the wall and the cables have to enter there regardless.

I have heard of some inspectors that require nail plates where the wires enter the box. Fortunately that's a non issue around here.
 