Hello,
Below is a picture of an installation that an electrical inspector called out 300.4 violation. The actual commentary was "300.4 (Box) protection". He said either the box needs to be raised higher or the ground lower.
I am not aware of a minimum height requirement for junction boxes. I am aware of protection of damage for cables and raceway as found in 300.4. It generically says that "Where subject to physical damage, conductors, raceways, and cables shall be protected." It does not mention boxes.
I was thinking maybe he was alluding to the PVC schedule 40. Which would say is susceptible to physical damage, it needs to be schedule 80. This is in a flower bed next to the house. How is it susceptible to physical damage? How does it apply to boxes? why was he making a distinction of the height of the box?
The closest thing I can find is 300.5 which is regards to underground installations. There is part (D) which reads "Direct-buried conductors and cables shall be protected from damage in accordance with 300.5(D)(1) through (D)(4)." In particular (D)(4) reads: "Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in electrical metallic tubing, rigid metal conduit, intermediate metal conduit, RTRC-XW, Schedule 80 PVC conduit, or equivalent." Is that in regards to enclosures underground? How can an enclosure be subject to physical damage underground? If it is regarding enclosures that are above ground that have underground conduits feeding into it, how does the conduit type matter in regards to the enclosure damage?
Anyone have any insight?

Below is a picture of an installation that an electrical inspector called out 300.4 violation. The actual commentary was "300.4 (Box) protection". He said either the box needs to be raised higher or the ground lower.
I am not aware of a minimum height requirement for junction boxes. I am aware of protection of damage for cables and raceway as found in 300.4. It generically says that "Where subject to physical damage, conductors, raceways, and cables shall be protected." It does not mention boxes.
I was thinking maybe he was alluding to the PVC schedule 40. Which would say is susceptible to physical damage, it needs to be schedule 80. This is in a flower bed next to the house. How is it susceptible to physical damage? How does it apply to boxes? why was he making a distinction of the height of the box?
The closest thing I can find is 300.5 which is regards to underground installations. There is part (D) which reads "Direct-buried conductors and cables shall be protected from damage in accordance with 300.5(D)(1) through (D)(4)." In particular (D)(4) reads: "Enclosure or Raceway Damage. Where the enclosure or raceway is subject to physical damage, the conductors shall be installed in electrical metallic tubing, rigid metal conduit, intermediate metal conduit, RTRC-XW, Schedule 80 PVC conduit, or equivalent." Is that in regards to enclosures underground? How can an enclosure be subject to physical damage underground? If it is regarding enclosures that are above ground that have underground conduits feeding into it, how does the conduit type matter in regards to the enclosure damage?
Anyone have any insight?