I was asked by the chief of my department to put this situation out and see what responses come back. One of our local utilities requires that conductors coming into a meterbase from an underground conduit run have large loops, that they call an "Edison heart". When a contractor doesn't include these in his installation, we leave a red tag that lists 300.5(J). We apply this to all installations that use an expansion joint and not just where required by this one electrical utility.
There is a contractor that believes that if he adds an expansion joint to his underground riser, as spoken about in the FPN, then he has complied with the requirement. He doesn't seem to understand the difference between a FPN and an exception.
What is commonly required in your area on conduit runs with an expansion joint ? What do you do to make sure that "cables shall be arranged so as to prevent damage to the enclosed conductors" ?
David
There is a contractor that believes that if he adds an expansion joint to his underground riser, as spoken about in the FPN, then he has complied with the requirement. He doesn't seem to understand the difference between a FPN and an exception.
What is commonly required in your area on conduit runs with an expansion joint ? What do you do to make sure that "cables shall be arranged so as to prevent damage to the enclosed conductors" ?
David