In 300.50(A), there are 3 categories of permissible installation that UG for >1000V must follow. The 3 options have the following titles:
300.50(A)(1) - Shielded Cables and Nonshielded Cables in Metal-Sheathed Cable Assemblies.
300.50(A)(2) - Industrial Establishments
300.50(A)(3) - Other Nonshielded Cables
Root Question: Does 300.50(A)(1) mean "Shielded Cables in Metal-Sheathed Cable Assemblies" and "Nonshielded Cables in Metal-Sheathed Cable Assemblies", OR is it "Shielded Cables" and "Nonshielded Cables in Metal-Sheathed Cable Assemblies"? The second way meaning that shielded cables without a metal sheath apply to this (A)(1).
My first interpretation of this section was that (A)(1) applies only to MC similar type... both for shielded and nonshielded... having that corrugated metal sheath like MC. But after looking at the rest of this section, I think (A)(1) applies to shielded cables without the metal sheath as well. So (A)(1) should be read as "Shielded Cables" and "Nonshielded Cables in Metal-Sheathed Cable Assemblies". Otherwise, what is permitted for a shielded 5kV cable without metal sheath? (A)(2) is only up to 2000V, and (A)(3) is only about other nonshielded cables.
Some colleagues and I had a debate on this a month or two ago, and now it has come up again on another project. Thank you in advance.