jamesguy10
Senior Member
- Location
- Amsterdam NY
Yes, run from the meter pan to a trough, and bug off a SER cable or conduit feeding a 200amp panel in the house, and bug off to a conduit that feeds the garage. I don't believe you would need a disco for the garage, BUt im not sure because my code book is in the truck and i always need to use a disco due to a local jurisdiction.
BTW, When i use this install its when the house panel is more than 15-20' away from the meter. If the panel is just inside the wall, Run two conduits from the meter pan into two different 200 amp panels with main breakers in the house, and put a 100 amp breaker in one of those, and run 1.25" conduit from it to the garage, were you would install a 100 amp panel.
Also, Do you really need a 320/400 amp service? Maybe a load calculation would be worth it? A 200 amp service would be a lot cheaper, easier, and it may be sufficient
BTW, When i use this install its when the house panel is more than 15-20' away from the meter. If the panel is just inside the wall, Run two conduits from the meter pan into two different 200 amp panels with main breakers in the house, and put a 100 amp breaker in one of those, and run 1.25" conduit from it to the garage, were you would install a 100 amp panel.
Also, Do you really need a 320/400 amp service? Maybe a load calculation would be worth it? A 200 amp service would be a lot cheaper, easier, and it may be sufficient
I believe I have seen it done this way also. Are you saying place a trough outside, bug off to the 2 locations and place a 200 main panel inside ? Just out of curiosity would I also need a disconnect for the garage also at this point?