I am sizing conductors for a 3000A service, 480V, 3phase, 4 wire system. I plan to use 90 deg wire, THHN. I have not decided on what type of cable yet but for these calculations I used SE cable in raceway, underground. The ambient temp is earth temp, 20 deg C. This wire comes from the service transformer to metering then to a transfer switch (service entrance rated with 3000A 100% rated breaker)(all outdoors). So I didn't derate for higher ambient temperature but did uprate for 20 deg C by 1.08 per table 310.15(B)(3)(a).
I broke the 3000A down into 3 different raceways or 1000A per raceway. I did calculations based on 500, 600, 700 and 750 kcmil wire with a neutral ran with each raceway and it is a current carrying conductor. Here is the number of conductors I came up with:
Now if I figure out conduit fill, I am pushing into greater than 6" RMC conduit for each run (3 runs). Did I do something wrong? I have been beating this to death but keep coming up with the same problem. Should I be looking at a different cable type like MI or MC?
Does 310.15(B)(3)(3) allow nonderating if using USE cable in a trench (says "adjustment factors shall not apply to underground conductors entering or leaving an outdoor trench if those conductors have physical protection in the form of RMC, IMC, rigid PVC or RTRC having a length not exceeding 10' ")?
Any help or confirmation of my calculations would be appreciated. Thanks.
I broke the 3000A down into 3 different raceways or 1000A per raceway. I did calculations based on 500, 600, 700 and 750 kcmil wire with a neutral ran with each raceway and it is a current carrying conductor. Here is the number of conductors I came up with:
Total Current | Ambient Correction Factor | Number of CCC derate | ||
3000 | 100% | 50% | ||
Number of Parallel Runs | 3.00 | |||
Current per Run | 1000.00 | |||
Corrected Ambient Current | 1000 | |||
Corrected CCC (10-20 CCC's) | 2000 | |||
# of conductors per phase (90 deg wire) | Number of CCC (exclude neutral) | # of CCC's with neutral | ||
500kcmil | 4.306632214 | 5 | 15 | 20 |
600kcmil | 3.898635478 | 4 | 12 | 16 |
700kcmil | 3.561253561 | 4 | 12 | 16 |
750kcmil | 3.461405331 | 4 | 12 | 16 |
Now if I figure out conduit fill, I am pushing into greater than 6" RMC conduit for each run (3 runs). Did I do something wrong? I have been beating this to death but keep coming up with the same problem. Should I be looking at a different cable type like MI or MC?
Does 310.15(B)(3)(3) allow nonderating if using USE cable in a trench (says "adjustment factors shall not apply to underground conductors entering or leaving an outdoor trench if those conductors have physical protection in the form of RMC, IMC, rigid PVC or RTRC having a length not exceeding 10' ")?
Any help or confirmation of my calculations would be appreciated. Thanks.