Things have changed a lot on this project and another has already started. They have minor differences. Below is a summary of what was done and what will be done at the next project. Sorry if my original post was all over the place.
We have settled on 8 runs of conduit with 500MCM for phase wire. However, I disagree with some of the comments in here. Let me add some clarification and say I have 3000A service, 100% rated, and am using THHW in PVC conduit underground. Ambient of earth is 20 deg C. The parts not in earth are less than 10' or 10% of the run so I can use 20 ambient and have an adjustment factor of 1.11 and since we service L-N loads (and harmonics for that matter), the neutral is CCC. So I have to derate 80% for 4 CCC's in one raceway.
From what I understand, you can't use the 90 deg column unless the terminals are rated at 90 and they are not, they are rated for 75 deg C. 500MCM can carry 380A (75 deg C terminals, our wire is 90C). So I adjust this by 1.11 then multiply times 80%: 380*1.11*80%=337A. This times 8 (8 runs of A,B,C) is only 2700A. We do have 277VAC loads tied to this service. Do you guys agree with this calculation?
So 8 runs of 500MCM is not sufficient. If I could eliminate my neutral load, then I can eliminate the 80% derating, which would allow me to use 500MCM with 8 runs in 4". We do have other L-N loads but they are serviced through a 'separately derived system' (transformer) so I am not counting these as L-N loads for the sake of CCC's derating. Assuming loads on separately derived systems don't qualify as L-N loads for the number of CCC derating, I may still be able to eliminate my 277V loads (LED's and Heat Trace) in order to get away with 8 runs of 500MCM (no CCC derating).
Thanks!