powerpete69
Senior Member
- Location
- Northeast, Ohio
- Occupation
- Professional Electrical Engineer
The breaker curve also appears to show that the 600 amp breaker should have tripped as well at 5.13kA........does anyone have an explanation for why it didn't per the breaker curve? The left side of that 600 amp breaker curve appears to be at 2.8kA. Perhaps the actual ground fault current was lower than that? Perhaps the 600A breaker curve does not meet its reality?