Yep. And RTFM means Read The Factory Manual...Reminds me of the naval avionics tech who had a shelf of modules marked "NFG". When a female officer asked him what that meant he replied, "Non-functioning gear, maam."
Would that be half the size of a Grunion? My spelling may be off.There’s a unit of measure I haven’t used in quite awhile.
Continuing slightly off topic.....Yep. And RTFM means Read The Factory Manual...
When they say flywheel, are they perhaps meaning flywheel energy storage? This could be used as the inertia needed to support the few seconds power surge caused by the load on the blade. Essentially helps the electric system ride through the fluctuations so the utility is isolated from the effect.
Seems you would need to hit an awful big and very hard spike or chain to even make a 300 hp motor groan just a little.Well, I haven't seen it all, but how would you make that work? If you use a chain or a belt to connect the blade and the flywheel you run a very high risk of busting the belt or chain if the saw tries to really decelerate if it hits a tough spot or (God forbid) a spike or piece of embedded chain (it has happened). That leaves making the flywheel a part of the saw blade assembly. Sounds like the definition of the word "kludge".
NEVER place fuses between the VFD output and the motor, it's a great way to destroy a VFD..."... the locked rotor current of a 480V – 3Phase, 300HP motor is 2200A"
This quote stood out in my mind as the answer. Unless I missed it, I haven't seen what I consider to be a simple suggestion. Your Customer already has the VFD to produce the Soft Start. Why not place Fast Blow Fuses between the VFD and the Motor. Select the Size that is appropriate to protect against Motor Lockup and propose it to the POCO. That way if something actually did lock up the Motor it might even protect the VFD, POCO, and the Motor. Just a thought.
Yep. Waste of time. Apart from anything else, the inverter would probably shut off on IGBT desat long before there was enough energy dissipated in the fuses to blow them.NEVER place fuses between the VFD output and the motor, it's a great way to destroy a VFD...
There is not going to be any "inrush current" when using a VFD, and if you can't stand the current it takes to create the torque that the motor may WANT to develop, then the VFD can be programmed to prevent that from happening, as previously discussed. It's just that there are consequences that must be considered. But don't go adding hardware to it like fuses on the output, the consequences are worse.
+"... the locked rotor current of a 480V – 3Phase, 300HP motor is 2200A"
This quote stood out in my mind as the answer. Unless I missed it, I haven't seen what I consider to be a simple suggestion. Your Customer already has the VFD to produce the Soft Start. Why not place Fast Blow Fuses between the VFD and the Motor. Select the Size that is appropriate to protect against Motor Lockup and propose it to the POCO. That way if something actually did lock up the Motor it might even protect the VFD, POCO, and the Motor. Just a thought.