bill@usps06492
Member
- Location
- Connecticut
I will be installing a 300kva XF 3ph 480p/208-120s (800a panel on the secondary) . I've cal'd the primary at 480v@500a ocpd, on the seconday I've come up with 833a@208-120 and decided to keep the ocpd secondary at 800a because none of the loads are continous, and because of the length of the run on the primary, I didn't want to over stress the transformer. The length of the run is my cocern! It's over 550ft from the primary circuit breaker to the spot where the XF is to be installed. At 500a I could use 250kcmil THHN parralleled with a 2awg cu ground in a 2.5" emt, but because of the length of the run, and I am using 600ft as the max distance, I'm concerned about the voltage drop. On a 408v circuit 14.4v=3%vd, and when I did my calculations I need a 350kcmil conductor, and a 3" conduit to get my 3% max vd.
300 x 1000/480 x 1.73= 361.4a
361.4a x 1.25%= 451.7 (500a ocpd primary)
300 x 1000/208 x1.73 = 833.3a (800a secondary)
cm = 1.72 x12.9 x 361.4a x 600ft/14.4vd
cm = 4839218.28/14.4 = 336056.825cm per ch9 table 8 is a 350kcmil and because the ocpd is 500a on the primary I need to size my wire to the 500aocpd, and thats 2sets of 350kcmil.
On the secondary it will be 2 sets of 600kcmil with a 1/0 awg cu ground. From the xf to the 208-120/800a panel is less tha 20ft.
So after all this am I on the right track, or am I over sizing my feeders? I will be using this information to order the material to do this job, and the price just for the panels, breakers, and the transformer is almost $10k, and God only knows what the wire is going to cost.
The loads to be servered for now,will be 3 pieces mail processing equp, with a max ocpd for the circuits @208-120v/125a 3ph using 1/0 cu awg 5wire, a 225a panel to feed 4-30a/208 3ph central vacuum units, and any future needs.
Bill
300 x 1000/480 x 1.73= 361.4a
361.4a x 1.25%= 451.7 (500a ocpd primary)
300 x 1000/208 x1.73 = 833.3a (800a secondary)
cm = 1.72 x12.9 x 361.4a x 600ft/14.4vd
cm = 4839218.28/14.4 = 336056.825cm per ch9 table 8 is a 350kcmil and because the ocpd is 500a on the primary I need to size my wire to the 500aocpd, and thats 2sets of 350kcmil.
On the secondary it will be 2 sets of 600kcmil with a 1/0 awg cu ground. From the xf to the 208-120/800a panel is less tha 20ft.
So after all this am I on the right track, or am I over sizing my feeders? I will be using this information to order the material to do this job, and the price just for the panels, breakers, and the transformer is almost $10k, and God only knows what the wire is going to cost.
The loads to be servered for now,will be 3 pieces mail processing equp, with a max ocpd for the circuits @208-120v/125a 3ph using 1/0 cu awg 5wire, a 225a panel to feed 4-30a/208 3ph central vacuum units, and any future needs.
Bill