I pulled a fuse disconnect 3ph, 200amp, 480v and found a A3T200 protecting each leg. Looking at the fuses it says they are rated with 300v. That cant be right, can it? Is it protecting only the 277 to ground.
Will they fit in a 600 volt disconnect?It is not uncommon to find 300V Class T fuses.
They only fit into disconnects specifically designed for them.Will they fit in a 600 volt disconnect?
I don't see an attachment. Do you have some photo's?See attached
Are you saying that those fuses were in a 200 amp, 600 volt disconnect switch?
Nope. That fuse is only rated for 300VAC max, if you have 480V you need the A6T for 600VAC max. Doesn’t matter that the L-N is 277V, it’s based on the line volts.
That’s what my problem is.Are you saying that those fuses were in a 200 amp, 600 volt disconnect switch?
Do have some photos?That’s what my problem is