bunuelbresson
Member
- Location
- Detroit, MI
Hey guys,
An equipment has a FLA of 30A, and has a L6-30P plug, and should go into an L6-30R outlet.
If a 30A breaker is installed to protect the circuit, the circuit breaker would generally be rated at 80% so would not be able to take a full 30A load. And we are not allowed to install a 40A breaker since the circuit would have a rating higher than the outlet can tolerate.
What is the solution?
Thanks
An equipment has a FLA of 30A, and has a L6-30P plug, and should go into an L6-30R outlet.
If a 30A breaker is installed to protect the circuit, the circuit breaker would generally be rated at 80% so would not be able to take a full 30A load. And we are not allowed to install a 40A breaker since the circuit would have a rating higher than the outlet can tolerate.
What is the solution?
Thanks