That is the rating of the device, not the listing information.
Can you land 12 AWG conductors on a 30 amp switch? Even a 60 amp switch?
It might be somewhat rare you would land 12 AWG on a 30 amp receptacle, but I don't think it is prohibited either.
termination smallest conductor is for a 10# it list it -- 12# under its terminal is non compliant --- why are you discussing switches in a receptacle discussion???? BTW they allow 14# guage under their termination