Why? The OCD protects the conductors, who cares what amperage rating the receptacle is? (as long as its a single receptacle)
I'm not really concerend about the receptical. I'm concerned about the
equipment actually as I think about it. I know these machines quite well.
The NEC is a safety manual. I work in Labs everyday and I started thinking.
Lets say I designed this and I wired it per the NEC. Is it compliant yes,is it
safe yes. Now as a design it is terrible. Your a researcher in a lab and you
have deadlines to meet protocals to follow. You place your product in this
centrifudge for 5 hours at a predetermined RPM at a certain temp so that the
FDA will accept your test results. Now the breaker trips two hours in the
process, over and over again. Are the conductors protected,yes, Is this a
compliant install yes,does it function, no. I have to stop thinking
the bare minium safety compliance is all I have to meet in order to feel
I did a good job. This post has taught me that the NEC is important
to human , property safety,but propper design along with NEC compliance
is how things should be done. The NEC is not the be all end all. If it
were why would we need engineers or designers? Ok yes I'm on a
NEC forum, so let me have it, I'm old and can take it.:smile: