kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Surge protectors are for absorbing brief transients and not for clamping continuous overvoltage conditions.
I am not going to be much help with determining if there is RF issues causing this.
Try turning off all power and disconnecting the grounded service conductor as well as any other grounding conductors that leave the premises and then checking for these stray voltages again. If isolated from outside by incoming conductors/conductive objects such as water, gas piping, communications cable shields, etc. and you still have voltage then it is coming from within and the RF could be a possibility.
I am not going to be much help with determining if there is RF issues causing this.
Try turning off all power and disconnecting the grounded service conductor as well as any other grounding conductors that leave the premises and then checking for these stray voltages again. If isolated from outside by incoming conductors/conductive objects such as water, gas piping, communications cable shields, etc. and you still have voltage then it is coming from within and the RF could be a possibility.