kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
If you chart the size vs ampacity, in sizes greater than 1/0, its no longer proportional. The ampacity of 500 mcm is not double that of 250.
So with larger services you get more ampacity per $$ by running in parallel.
If a conductor is parallel to another conductor with control wiring it generally isn't for the purpose of attaining a higher overall ampacity conductor out of multiple sub elements like it is for power conductors.Good stuff.
“Engineering supervision” is allowed in Exception 2....so why can’t it be the same for new installations?
Exception 1 allows control cables to be in parallel for voltage drop to instruments. Go figure....
This one area of the Handbook that could use some enhanced explanation.
Sent from my iPhone using Tapatalk
Handbook is useful but commentary portions is not official NFPA interpretation of the code either. It does mention this right at the front of the book. Any such enhanced explanation is from opinion and reasearch done by those that write such explanation and not an official NFPA explantion. If you can find when such language is adopted and find the ROP's you should find out why the CMP made the decision they made at that time to put in the language they put in.