j_erickson said:R is 4 conductor, U is 4 conductor.
...although I don't see an "R" anywhereType SE, cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
Type USE or USE-2, cable for underground installation, including burial directly in the earth....Types USE and USE-2 are not suitable for use in premises or above ground except to terminate at the service equipment or metering equipment.
j_erickson said:R is 4 conductor, U is 4 conductor.
tmbrk said:The southwire link I listed in my last post states under cable "construction" that the SER has a reinforcing tape under the jacket and the SEU does not.
Dennis Alwon said:Ser is a 4 wire service cale while seu is a 3 wire cable. USE is underground cable. I do not know what the U and R stand for.
j_erickson said:Thanks for the correction Dennis. That was a typo. I had to cut it short as something came up while I was posting.
Actually, they both have the reinforcing tape. From the Southwire website:tmbrk said:The southwire link I listed in my last post states under cable "construction" that the SER has a reinforcing tape under the jacket and the SEU does not.
Southwire Type SE, Style U Cable assembly plus an overall concentrically applied neutral and reinforcement tape are jacketed with gray sunlight resistant polyvinyl chloride (PVC).
iwire said:.... At one point typical SE cable was armored....
Mike NY said:I always assumed SEU was a 3 wire cable with the neutral being bare and wrapped around the other two cables. SER cable having all conductors with insulation and having a bare ground sized correctly. Both with the same outer covering.