EEEC
Member
- Location
- Benicia, CA, USA
So I've got a 600A rated panelboard being fed by a 600A main breaker (all specified in the architectural drawings). According to 310.15(B)(16), I would need to use 1000 kcmil. So why does the MB only accept up to 750 kcmil? And secondly when I approached the supplier for a cost on the 1000 kcmil, he acted as if I was crazy and said they don't carry that size and would have to hunt around. Am I missing something here or figuring wrong? :huh: