Just went lookinI at my fresh 2014 and there is no 310.13.
Infinity/Rob has the current reference.
Last edited:
:slaphead: I need to burn some new neural pathways.Rutrow.
Just went lookinI at my fresh 2014 and there is no 310.13.
ZKST Thermoset-insulated wire
XHH ? Indicates a single conductor having a cross-linked synthetic polymer insulation with no overall covering provided, rated 90?C dry.
XHHW ? Indicates a single conductor with the same description as Type XHH, except that it is rated 90?C dry, 75?C wet.
XHHW-2 ? Indicates a single conductor with the same description as Type XHH, except that it is rated 90?C dry, 90?C wet.
Well that pretty much screws my opinion
Still have issues with way XHHW without -2 is in the 90 C. Column
That is because it can be used in the 90C column if it is not in wet location. I don't know how else they can explain it in the table.
That's what I do.XHHW
continuous load
ambient temp correction
75C lugs
Larger of these two:
Ampacity of XHHW from 75C column x 1.25 then pick wire size from 75C
Temp correction / ampacity rating from 90C column then pick wire size from 90C
Choose the larger wire size for calculation.
This is how I would do this. Is this correct?
Just thought of something, I pretty sure you don't have to use the temp correction for xhhw under 2014.Temp correction / ampacity rating from 90C column then pick wire size from 90C
Yep, well you should know, I guess.
I always use XHHW-2 so this never came up. Interesting.
Digging into this calculation further, situation with all the following variables:
XHHW
continuous load
ambient temp correction
75C lugs
Larger of these two:
Ampacity of XHHW from 75C column x 1.25 then pick wire size from 75C
Temp correction / ampacity rating from 90C column then pick wire size from 90C
Choose the larger wire size for calculation.
This is how I would do this. Is this correct?
You still have to do the temperature corrections for XHHW, but you don't have to add the temperature adder shown in Table 310.15(B)(3)(c) if you are using XHHW conductors.Just thought of something, I pretty sure you don't have to use the temp correction for xhhw under 2014.
310.15(B)(3)(c) Raceways and Cables Exposed to Sunlight on Rooftops.
Where raceways or cables are exposed to direct sunlight on or above rooftops, the adjustments shown in Table 310.15(B)(3)(c) shall be added to the outdoor temperature to determine the applicable ambient temperature for application of the correction factors in Table 310.15(B)(2)(a) or Table 310.15(B)(2)(b).
Exception: Type XHHW-2 insulated conductors shall not be subject to this ampacity adjustment.
No I was saying 90C wet for xhhw-2 but not for xhhw.I guess I'm confused.I thought Dennis was saying XHHW-2 was only rated 75 wet