Re: 310.15(B)(6) and NM
2005 - 310.15 (B) (6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For individual dwelling units ----Table 310.15(B)(6), shall be permitted ---- feeder conductors that serve as the main power feeder to each ----
For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).
2002 - 310.15 (B) (6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For dwelling units, conductors, --- Table 310.15(B)(6), shall be permitted as --- feeder conductors that serve as the main power feeder to a dwelling unit ----
For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboard(s) .
I read both of these to say about the same thing, ?AND FEEDER CONDUCTORS THAT SERVE AS THE MAIN POWER FEEDERS.?
I think this means that Table 310.15 (B) (6) can?t be used to size conductors for any sub panel from a lighting and appliance panel board as defined by ?02 in 408.14 (A) and 408.34 (A) in the ?05 code. (10 percent of its overcurrent devices protecting lighting and appliance branch circuits.)
Table 310.15(B)(6) Conductor Types and Sizes for 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. Conductor Types RHH, RHW, RHW-2, THHN, THHW, THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE, USE, USE-2
NM cable is not listed above so if this is the main power feeder NM cable would not be allowed.
If this is a sub panel feed from a lighting appliance panelboard then three conductor with ground NM cable will be fine if sized from Table 310.16.
110.14 (C) (1) (2) both codes allow the use of the 75 degree column