This wasn't covered in the FAQ, but I've been told several times by various electricians that you can no longer use table 310.15(B)(6) to size a feeder to a sub. The only explanation that I've gotten is, "The wording has changed".... So... I looked it up and it does seem fairly cut and dry but I want to make sure before I file it away upstairs.
You can see the highlighted text directly above the table and my summary would go like this:
"For the purpose of this article, A Main Power Feeder is one that shall supply All loads that are part of the dwelling."
That pretty much rules out your standard sub panel.... No? So, #2 AL for a 100 panelboard is no longer allowed and you must use 1/0 according to Table 310.16, right?
Thanks all.
Jon
You can see the highlighted text directly above the table and my summary would go like this:
"For the purpose of this article, A Main Power Feeder is one that shall supply All loads that are part of the dwelling."
That pretty much rules out your standard sub panel.... No? So, #2 AL for a 100 panelboard is no longer allowed and you must use 1/0 according to Table 310.16, right?
Thanks all.