Show him this It would apply if there were one panel feeding all loads.
What Dennis is saying is correct. If you installed a meter combo with say an 8 circuit panel built in. If you feed something like an outside A/C or well pump or whatever then you could not use table 310.15 (B)(6) for the feeders I.e.: 2/0 Cu. But if you brought those same loads back out of the main panel then you could use 2/0. So by the way it is written in the case of a meter combo with branch circuits you must increase the wire size for lowering the amp load on the wire. :?:?:?
So if I have a 24 circuit meter main outside with a subpanel inside of the dwelling, then I can not use 310.15(b)(6) for the service conductors???
However, I can use 310.15(b)(6) if ALL of my load and branch circuits are fed from the meter main combo and there is no subpanel anywhere.