200A service for single family residence (in Seattle)
Demand load calcs come out at 105A for load and 65A neutral. So we have already installed 4/0-4/0-2/0 AL Triplex from the weather head. Original plan was to have panel back to back with meter but now the room is supposed to become a bedroom and GC wants to move the panel about 25 ft away on interior wall.
At this point, we were planning to swap the meter for a meter/distribution panel with 200A OCPD at the meter, then use feed-thru lugs to run 4/0 AL SER cable to a 200A MLO panel at the new location; so all protection at the meter.
If we want to run feeders from the meter/distribution to detached garage and a detached (finished) out-building (not a dwelling) can we do so and still use 310.15(B)(6) to size the SER at 4/0 or (as I've seen in other threads) does 310.16 apply in that case? Isn't the remote panel STILL taking all the load for the dwelling and therefore should 310.15(B)(6) still not apply? OTHERWISE, do we need to put a smaller breaker at the meter or use a 150 at the remote panel (MBP then)?
Demand load calcs come out at 105A for load and 65A neutral. So we have already installed 4/0-4/0-2/0 AL Triplex from the weather head. Original plan was to have panel back to back with meter but now the room is supposed to become a bedroom and GC wants to move the panel about 25 ft away on interior wall.
At this point, we were planning to swap the meter for a meter/distribution panel with 200A OCPD at the meter, then use feed-thru lugs to run 4/0 AL SER cable to a 200A MLO panel at the new location; so all protection at the meter.
If we want to run feeders from the meter/distribution to detached garage and a detached (finished) out-building (not a dwelling) can we do so and still use 310.15(B)(6) to size the SER at 4/0 or (as I've seen in other threads) does 310.16 apply in that case? Isn't the remote panel STILL taking all the load for the dwelling and therefore should 310.15(B)(6) still not apply? OTHERWISE, do we need to put a smaller breaker at the meter or use a 150 at the remote panel (MBP then)?