aftershock Senior Member Location Memphis, TN Oct 16, 2012 #1 This table is for 120/240-volt 3 wire single phase. Is there a table for 4 wire 120/208 volt 3- phase?
This table is for 120/240-volt 3 wire single phase. Is there a table for 4 wire 120/208 volt 3- phase?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Oct 16, 2012 #2 aftershock said: This table is for 120/240-volt 3 wire single phase. Is there a table for 4 wire 120/208 volt 3- phase? Click to expand... Yes it is called 310.16
aftershock said: This table is for 120/240-volt 3 wire single phase. Is there a table for 4 wire 120/208 volt 3- phase? Click to expand... Yes it is called 310.16
aftershock Senior Member Location Memphis, TN Oct 16, 2012 #3 Thank you. I did not see "service" listed in that table.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Oct 16, 2012 #4 310.16 works for services, feeders, and branch circuits. 310.15(B)(6) works only for services, and only under limited circumstances.
310.16 works for services, feeders, and branch circuits. 310.15(B)(6) works only for services, and only under limited circumstances.