kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Neutral doesn't need to be same size as the ungrounded conductors in many cases. The more "line to line" loads you have the less neutral load you will have to account for. Say you have 100 amp feeder and 40 amps of straight 208 volt loads, there is no reason your neutral should need to be more than 60 amps out the starting gate. The clueless inspectors out there probably won't see it this way though