DBoone
- Mississippi
- General Contractor
Why does 310.15(B)(7) allow 2/0 copper for a 200A service or feeder but then flip over one page to 310.15(B)(16) and 2/0 copper isn't rated 200A even at 90C.
Ever look at the size of wire the POCO attaches to those 2/0 conductors?Why does 310.15(B)(7) allow 2/0 copper for a 200A service or feeder but then flip over one page to 310.15(B)(16) and 2/0 copper isn't rated 200A even at 90C.
That is only for a residential service, also the 2014 NEC scrubbed that table so now you must do the math.
Actually it is because the calculations in Article 220 are very very conservative and result in the requirement for a service that is much larger than needed in the real world. The residential service wire sizes came from actual loads from the utility companies....
The reason the NEC allows this reduction for residential work is because of the diversity of the loads. Commercial loads such as lighting etc are going all the time. In residential loads are on and off so frequently that there generally is never a high demand on the service conductors.
Line trucks only have two sizes for service drops, 2 and 6. POCO has been making these connections for a long time so they know what worksEver look at the size of wire the POCO attaches to those 2/0 conductors?
This is true but that table will work without doing the math. The math will come out to be what the table would be. For a 200 amp service you multiply by 83% and get 166 amps. Table 310.15(B)(16) allows 2/0 copper since it is rated 175 amps at 75C. The catch here is if you use se cable and it is rated 60C you will have issues where in the Table that really never addressed all the other factors.
You are right and that was my point. Don explained it better and more completely.Line trucks only have two sizes for service drops, 2 and 6. POCO has been making these connections for a long time so they know what works
But they are not insulated, but rather covered, and are considered single conductors in free air.