24 hot #12thhn with 8 #12thhn neutrals pulled in a 2"aluminum conduit from a 3 phase panel to feed lighting and receptacles do these conductors need to be derated as shown in 310-15 if so does the neutrals count in the total or just the hots
 
Re: 310-15

Yes, you will have to derate these conductors.

As far as the neutrals, are the loads linear or non-linear loads? Read 310.15(B)(4)(b)

Roger