When feeding a dwelling service via 120/208 1phase, can you use 310.15b?
When feeding a dwelling service via 120/208 1phase, can you use 310.15b?
Yes, quite common in cities, well at least in my area.
How did a garage get into the picture?It's not mentioned in the OP.![]()
208 in resi in mass ???? where?
The garage is inside?!?!?!![]()
How did a garage get into the picture?It's not mentioned in the OP.![]()
C. 120/280 volts, single phase, 3 wire, service
Normally available only in the Downtown Boston Network
District for connected loads not greater than 200 amperes.
This service may be available upon consultation with
NSTAR. Larger services must be three phase, 4 wire.
Never have seen it. So why do you suppose T310.15(B)(6) only applies to 120/240 services? Any ideas other than that's what the code states? :smile: