Re: 310.16 correction factors

Originally posted by stew:
I am also trying to see whether the lugs might be rated for 90 deg and then use a 225 amp breaker rated 90 degrees and the problem would be eaqsily solved.
I believe there is a code section that states you can never use the 90 deg except for derating for voltage drop and temp and stuff.
 
Re: 310.16 correction factors

actually you can use the 90 deg table as long as you use a compatible device.But I have since found that the feed thru lugs are only rated 75 deg so I am back to square one.Cant find a 90 deg lug.

[ May 05, 2004, 02:59 PM: Message edited by: stew ]
 