I started an install today that requires adding two more 2" EMT runs to an existing rack of four. Each EMT contains or will contain three 3/0 and the EMT is the EGC.
These are/will be parallel conductors.
The the project PM looks up at the first 150' run and says I can't use set screw fittings, he just got a pdf spec requiring compression.(after contract is signed???)
I tell him I have to match existing as per this:
These are/will be parallel conductors.
The the project PM looks up at the first 150' run and says I can't use set screw fittings, he just got a pdf spec requiring compression.(after contract is signed???)
I tell him I have to match existing as per this:
So if I have 4 raceways existing with set screw fittings and add 2 with compression fitting, do my raceways have the same characteristics???310.4 Conductors in Parallel.
(C) Separate Cables or Raceways. Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics.