I installed 7 sets of 300mcm for a 2000 amp ct cabinet which totals 1995 amps
, i was told to add 1 set OF 300mcm because i'm short 5 amps:rant:, i couldn't run the new set underground as the old one so i ran it in rigid conduit above ground, the original sets of conduits are about 9 feet long and the new one is about 8 foot long, now i got a violation that it does not conorm with 310.4 that it has to be the same length, i took a reading on the wire and the new wire is with in a 3 amp range of the old, can someone advise how i can convince the inspector that i am conforming with 310.4:angel:
I am basing this response on 2008 NEC because 2011 does not have a section 310.4.
I did not check your conductor ampacities, but assuming you do have an ampacity of 1995, that is a violation of 240.4(C). If the overcurrent device is over 800 amps you can not round up to next higher overcurrent device - you must have conductor that meets or exceeds the overcurrent device in ampacity.
Next part, 310.4(C) says:"Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics".
You said you ran RMC above ground for the additional set of conductors you installed. Not only do the conductors need to be same size, type, length, they need to be in same type of raceway to achieve same electrical characteristics. Should your underground raceways be PVC and your above ground raceway be RMC - you will have a definite difference in impedance in conductors in one of the underground raceways than you have in the above ground RMC - especially during high current instances like a short circuit or ground fault.
When you compared amps on the additional conductors to that of the original conductors, what kind of load was on the service? If it was lightly loaded your reading of only 3 amps difference may have very little value compared to if you were running near full capacity.
Other possible directions to go with this?
Do you have a single 2000 amp overcurrent device that this is protecting this?
It would be possible to have your original 1995 amps worth of conductors supplying multiple service disconnecting means as long as the calculated load was 1995 or less amps, and you could even have more than 2000 amps total service disconnecting means and still be ok with those same conductors.
I know, all that over 5 amps of capacity, but that is what is written in the book.