I believe any opening larger than 1/8" would negate the Type rating of the enclosure. So, if you used a clamp in that 1" KO you would probably be okay..... but could you just use a 1" KO if you wanted to?
It's strange that the NEC doesn't have any guidance on this. It simply requires an unused open to be closed. A 1" KO with a GEC run through it would not be unused so it would not require some type of closure.I believe any opening larger than 1/8" would negate the Type rating of the enclosure. So, if you used a clamp in that 1" KO you would probably be okay.
And along with that the same thing could be said about surface mount dryer receptacles.It's strange that the NEC doesn't have any guidance on this. It simply requires an unused open to be closed. A 1" KO with a GEC run through it would not be unused so it would not require some type of closure.
Isn't closing is to prevent people contact? Ventilated transformers are clearly not insect or mice proof.It certainly is not closed to insects or even mice. Not my picture but I've always wondered about it.
I think it's both. Rodents and insects can cause a lot of damage in load centers and devices. I don't think ventilated transformers would be quite as much a concern, but that is just my thoughts.Isn't closing is to prevent people contact?