In the Nov 08 NEC questions & answers from M Holt, there was a question about more than 1 NM cable through a KO.
Here is the question and answer:
Q8. Can we put multiple NM Cables through a single knockout in a panel?
A8. No, cables must be secured to the enclosure with fittings designed and listed for the cable [312.5(C)].
I don't see any text in 312.5(C) that says I cannot put 2 ROMEX cables in a ROMEX cable clamp.
Can anyone clear this up for me??
Thanks.
Here is the question and answer:
Q8. Can we put multiple NM Cables through a single knockout in a panel?
A8. No, cables must be secured to the enclosure with fittings designed and listed for the cable [312.5(C)].
I don't see any text in 312.5(C) that says I cannot put 2 ROMEX cables in a ROMEX cable clamp.
Can anyone clear this up for me??
Thanks.