Great question I have often wondered this myself. I believe the 18" is to keep any sparks etc from exiting the conduit if a short should occur inside the panel. Just a guess. I assume surface because they want the conduit visible for inspection.-- Another guess. I guess crap can also fall into the pipe easily if it is less than 18". Needless to say, I have seen it way to often where a 2"pvc conn is installed in the top of a panel ( both recessed and exposed) with many nm cables installed thru it.Why can't the Raceways entering the top of a Surface Mount Enclosure be less than 18" ? Where did this measurement come from and what diffference would it make if it were Less?
Also, Why is this only allowed on Surface Mount Enclosures and not Recessed?
Also, Why is this only allowed on Surface Mount Enclosures and not Recessed?
312.5 C Indicates Surface Only, Not Recessed Installations.
Help me out here, I don't see that.
312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of this article shall be protected from abrasion and shall comply with 312.5(A) through (C).
(A) Openings to Be Closed. Openings through which conductors enter shall be adequately closed.
(B) Metal Cabinets, Cutout Boxes, and Meter Socket Enclosures. Where metal enclosures within the scope of this article are installed with messenger-supported wiring, open wiring on insulators, or concealed knob-and-tube wiring, conductors shall enter through insulating bushings or, in dry locations, through flexible tubing extending from the last insulating support and firmly secured to the enclosure.
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
Does this help old man.Help me out here, I don't see that.
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
Does this help old man.
- Another guess. I guess crap can also fall into the pipe easily if it is less than 18".
Also, Why is this only allowed on Surface Mount Enclosures and not Recessed?
Also, Why is this only allowed on Surface Mount Enclosures and not Recessed?